Dan Ritter wrote:
> Matt Shields wrote:
>> About a year ago I purchased 6 x APC SmartUPS 3000's...
>> If they've been sitting on a shelf since then, will they
>> still work and are the batteries still good?
>
> They should be in approximately the same state as when you
> bought them: if the controllers were good then, they'll be good
> now, and if the batteries were good then, they are only slightly
> less likely to be good now.
Probably true. Particularly if the batteries were charged when put into
storage and kept relatively cool.
Generally, it is recommended to charge lead-acid batteries every 3 to 6
months. More on storage here:
http://www.powerstream.com/Storage.htm
> Connect a small load -- say, a 100W lamp -- to the UPS, and fire it
> up.
Sounds fine. I wouldn't recommend doing a full discharge runtime test.
(Apparently some people do that on a regular basis and APC has taken to
printing warnings in their literature not to do this, as it shortens the
battery life considerably.)
-Tom
--